Dear Friends,
we all know that we can get the Scan time of a Task using GSV Instruction. I would like to know is there any Method/formula to get the Scan time of the Controller.

Can any one tell me the relationship between Controller I/O-Memory & Scan time, How I/O memory is affecting the scan time of Controller?
 
CLX scan time

Hi,

In CLX you can monitor scan time for everything thru tool "task monitor". Install this tool and you can monitor performance of routines, programms, tasks , memory and CPU as well.
 
Thanks CLXenggr,
I want to monior the Controller scan time programmatically not via task monitoring tool, Do u any idea to accomplish the same, if have please let me know..
 
CLX ScanTime

As CLX is NOT a PLC, (it is PAC) the normal concept of scantime does not apply to it. Controller executes (scans) Tasks/programms and IO asynchronously hence like PLC you do not have scan, like Input scan, programm and output scan.
IO's are accessed as per RPI times or module's settings.
 
If you are looking for instantaneous scan time you can use a GSV in the continuous task to read the WALLCLOCK value (DINT[2] array) and take the delta of the LSW of the array between scans. This is a measure in microseconds of how long it took the processor to make one complete pass and get back to the continuous task. Keep in mind that this value can be extremely variable if you have multiple periodic tasks scheduled and/or alot of I/O. But I have found this to be the most accurate indicator of composite scan time available internal to the plc.

Keith
 

Similar Topics

Good morning. This is something new to me. we have an existing controller running one of our plants. we are doing a conversion on another...
Replies
7
Views
1,168
We have recently experienced two failures on our Allen Bradley Controllogix PLCs and I have been tasked with researching the problem and hopefully...
Replies
9
Views
2,268
I have to add some analog and digital IO modules to an existing project as the part of a modification.Client is asking for a remote IO rack and...
Replies
8
Views
3,669
I'm pulling out a Flex Logix controller and updating to a control logix 1756-L72. My question is will that just straight swap out? and do I need...
Replies
2
Views
3,263
How can I use 1761-NET AIC device to communicate with control logix 1756-L61 controller?? I want establish a communication between PLC and DCS via...
Replies
0
Views
2,234
Back
Top Bottom