ABB VFD Problem

rthiyagu_00

Member
Join Date
Nov 2006
Location
TRICHY 620013
Posts
26
We are having a ABB make VFD - ACS800 for fan application. It was commissioned and working for last three months. Now it is not responding to DCS input (4-20ma) and increse/decrese 24 V DC input from VFD panel for any increse/decrease command. Any change made from these two destinations leads to bringing the speed to ZERO with current indication in the existing value. However it is responding to HMI Keypad operation. No specific display in HMI screen.

Regards

R.Thiyagarajan
 
rthiy, I am very familiar with the ACS800 and will try to help you.

I am having a little trouble understanding your description of the problem. You mention a 4-20ma signal for speed and you also mention increase/decrease inputs on the 24VDC digital inputs.

Please check Group 99 Parameter 02 and advise what is entered there. That parameter (99.02) is where the Macro is entered which defines the configuration of all of the analog and digital input terminals.
 

Similar Topics

Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
120
Hello Experts, I recently stumbled with an issue about ABB VFD ACS800 connected with B&R PLC X20CP1484-1. This ABB VFD ACS800 somehow got...
Replies
0
Views
315
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
Replies
23
Views
2,574
Hello all. Working on a centrifuge for a customer. They have ACS880 ABB Vfd's installed, and need them to talk VIA the FENA card Ethernet to...
Replies
1
Views
1,340
I am using a 4-20mA signal from an RTD to an ABB ACH 550 drive. I want to know if anyone has ever set up a PID loop on one of these units before...
Replies
0
Views
1,112
Back
Top Bottom