we are adding sensors to a press and need a "slave" plc/smart relay to process those signals and then send a go/no go signal to the S5. I will probably use a transistor source plc or what ever to drive this "coupler" that will inturn send a pulse to an input to the S5. I haven't been able to find a Plc that will talk directly without electrical problems
You haven't explained why there are "electrical problems" connecting the output of your slave PLC to an input on the S5. There shouldn't be, especially with 24vdc. It's done all the time.
If you have to match up two different kinds of I/O, then a solid state relay makes sense. Once again, easy to do for the 24vdc side. If you have to do 120vac, you need a load resistor to deal with leakage current, but it's still pretty easy.
From what I can tell, your cycle is as follows:
700 cycles per minute
each cycle is 1/700*60 = 0.0857 seconds per cycle
Not sure what "sensors are muted" means but I'll assume that the sensors are always "off" for 350 degrees and can only be active for 10 degrees of rotation.
0.0857/360*10 = 0.0277 second window
A small PLC can respond in this time frame, but can you tolerate the delay? How much time do you have to get the "go" signal at the start of this window?
I'm going to make a suggestion... Read the document referenced in Rdrast's signature.
How to ask questions the SMART Way! I think you might find it beneficial, I know I did.
Good luck, and let us know how it works out.