As I understand it UL508A requires that all instrial control panels be marked with the overall SCCR of the panel and a method is established for arriving at this rating. I also understand that the US NEC states that a panel must have an SCCR greater than the available fault current available in the system into which the panel is being installed.

My question is I do not see anywhere in the Canadian Electrical Code that this is a requirement. Does anyone know the relevent section of the CEC?
 
I don't have the CEC with me right now and I can't think of a specific rule in it. However most electrical equipment is evaluated based on the CSA SPE-1000. The SPE-1000 rule 5.1(l) on marking states
(l)for electrical equipment required to interrupt current and rated at 750v and less, interrupting ratings in accordance with Part II standards. (To be plainly marked in a permanent manner)
 

Similar Topics

Hi all, we are assembling an industrial control panel which consists of 4 branch circuits supplied from panel feeder as follows: Panel feeder ...
Replies
5
Views
5,140
Is the SCCR value of 5kA the default value used if the device has never been tested? I have a 480 VAC demagnetizer with no SCCR and a 480 VAC...
Replies
0
Views
530
How do compact busbars affect SCCR? Specifically, I'm looking at Allen Bradley's 140M-C-W453N. I can't find any information. My thoughts are that...
Replies
2
Views
1,121
I have been going over my notes from a UL class from years ago and was trying to see what effect on SCCR a power distribution block would have in...
Replies
12
Views
3,361
Hoping there might be a SCCR guru that could guide me to an answer: I’m doing some retrofit projects where the panels have to be updated for SCCR...
Replies
2
Views
2,299
Back
Top Bottom