I have a Micrologix 1500 configured with a 1769-SDN communicating with 1769-OB32 24VDC output module using a 1769-ADN.

The Micrologix reads the adjoining module a 1769-IQ32 to memory address I:1.66 this one reads fine to the 1500.

The RSNetWorx shows that the 1769-OB32 is mapped to O:1.2 and O:1.3. When I activate any of the bits in ladder logic, the outputs do not switch.

Looking at RSNetWorx the 1769-ADN is not seeing any of the mapped outputs being sent.

Any ideas?
 
Let's visit the fundamentals:

Are there any errors indicated by the 1769-SDN display ?

Do you have the "Run" bit in the 1769-SDN Command Word (O:1.0/0) set true, with the MicroLogix 1500 in RUN mode ?

Inputs will read fine in controller Program mode or scanner Idle mode, but outputs will not be sent.
 
Let's visit the fundamentals:

Are there any errors indicated by the 1769-SDN display ?

Do you have the "Run" bit in the 1769-SDN Command Word (O:1.0/0) set true, with the MicroLogix 1500 in RUN mode ?

Inputs will read fine in controller Program mode or scanner Idle mode, but outputs will not be sent.



Hi.
I have de same problem, I have a remote backplane with 4 slots 2x iq32 and 2 oq32, the equipament works well, and quickly stop work and I have 2 iq32 without communication and 2 oq32 works. I can’t understand the command run for s
Slots. Can you explain please?
 
Hi.
I have de same problem, I have a remote backplane with 4 slots 2x iq32 and 2 oq32, the equipament works well, and quickly stop work and I have 2 iq32 without communication and 2 oq32 works. I can’t understand the command run for s
Slots. Can you explain please?

What is the PLC connecting to the remote rack?
 
That's an Ethernet adapter, not a DeviceNet adapter. And you revived this thread that had been resolved for almost 15 years.

Please go to the main PLCTalk Q&A page and click the green "Start a new thread" button. Post as much information about your system as you can.
 
What does the Module Info tab say?

What he said.....The rest of your modules are online, you have keying disabled, so likely a full module mismatch (wrong model). If you go to the module tab it will compare the online module found with your project and you can see the differences.
 

Similar Topics

Good Morning All, I worked with Automation Direct and Allen Bradley for the last 20 years. Now I have a new job working with Omron. My first...
Replies
7
Views
2,629
Hi all, I am currently working on a project involving the use of a Micrologix 1100 PLC with RSlogix 500. With the program downloaded to the PLC, I...
Replies
3
Views
2,520
Hello, I am new to this group and to the plc. I am trying to connect the plc-5 to my computer using usb serial adapter. I am going to configure...
Replies
17
Views
3,975
Hi I am having a problem with connecting to a plc at work.It is a modicon micro 110 CPU 411 00. I am trying to connect using Proworx 32 trial...
Replies
0
Views
1,303
I have a TP170A panel. I want to connect it to PLc via PROFIBUS. I use wincc flexible 2007 and STEP7 5.2. Meanwhile installation of WinCC fl. , it...
Replies
16
Views
5,862
Back
Top Bottom