Hi Hojland,

It will depend on the expansion slot number and the channel of that slot you are using...
For example, if you fit a 1762-IF4 and make it the first expansion module - and you want to address the first analogue channel of that module, you would use I:1.0 as the address in your code (in your case, the Input address of an SCP block). The spare channels would be I:1.1/I:1.2/I:1.3.

Hope this helps!

Regards,

Rob
 
šŸ™ƒ ...Sorry, forgot all about those ones!

Don't use the built in very often. From memory, i think the data range is something like 0-1023. I have used a 500ohm resistor across them and used 4-20mA transmitters (range is approx 202-1023)in the past, and they seem ok for basic process monitoring...

Hope this (also) helps!


Rob
 