Just looking for some advice on which AB Plc to go for.

The process has 500 I/O, All the I/O is in panels but will be split up into two with a remote rack. All the I/O are Digi and relay output with the execption of 8 analoque ouputs and 4 drives.

Also I will have 2 hmi's and about 4 drives. They are local to the panel but not sure on which network to use.

I have allways used Mitubishi but we have two systems on site that have the compact logic L35E so I was thinking of going down the same road.

However I'm not sure if I should go for the control logic range.

So just wondering which range is most popular amoungst professionals compact logix or control logix?

Andy
 
My take on what distinguishes a ControlLogix over a CompactLogix:
More powerful.
More communication possibilities.
Safety functionality.
RIUP.
I would say go CompactLogix and all ethernet, but AB's odd product family tree forces you to choose between devicenet, or select a different hardware family for the remote i/o.
There is an 1769-ADN adapter for putting 1769 i/o as remote racks on DeviceNet, but nothing like that for Ethernet/IP (as far as I know). Really strange, as it would have fitted nicely with the Ethernet/IP port on the 1769-L35E.

To my opinion, when you are making a strategic decision about which new PLC platform to use over the next many years, chose the one that is based on Ethernet if you can. Profibus and DeviceNet are not bad choices, but 10 years from now they will be less important than they are now.

So I think you have these options to choose from:
  • CompactLogix CPU and i/o + DeviceNet adapter + CompactLogix i/o on DeviceNet.
  • CompactLogix CPU + Point i/o on Ethernet/IP.
  • ControlLogix CPU + ENBT adapters + ControlLogix i/o on Ethernet/IP.
 
I'd suggest going with ControlLogix, especially if you will have potentially multiple communications networks.
To save some money, you can use 1734 Series Point I/O for the remote rack, which can be MUCH less expensive then a full 1756 rack.
 
I would say go with CompactLogix and 1794 Flex I/O for the remote panel. The Ethernet adapter for the Flex is 1794-AENT.
 

Similar Topics

Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
17
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
40
How to fix if appears code “$115 plc-restart running” on the screen OP17
Replies
1
Views
58
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
20
Views
153
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
54
Back
Top Bottom