PV+600 / ML1100 Ethernet Coms Issue....grrrr

Norml

Member
Join Date
Nov 2006
Location
Maine
Posts
212
Hi guys,

This morning I was called over to a machine that has been running fine for months. The screen had ?????s everywhere so that I know that it lost coms. I checked it with FT View ME and both the PV+ and the PLC show up when browsing. The target setup in RSLinx is still OK. I'm using fixed ip addresses so DHCP hasn't pulled a fast one on me. I took several shots at compiling and reloading the .mer but nothing changed. So - my last resort was to pull a spare PV+ (new) off the shelf and swapped it out. I still have ??????s everywhere so a new unit didn't fix the problem. I've done about a dozen of these setups so I thought I knew what I was doing. Any ideas?
 
Something else has 'appeared' on the network with the same address as the PV+?

Cabling between the PV+ and PLC.

PLC has exceeded its no. of connections, not sure what it is for the ML1100?
 
Hi guys,

Thanks for your input. It ended up being an intermittent cable between the PV+ and the ML1100. When I opened the panel door, the PV worked. It took a while to figure it out because when I closed the door to look at the screen it had already lost coms. Sheesh.

I fixed a strapping maching this morning by wiggling the connectors. Its amazing how many problems are the result of bad connections.
 

Similar Topics

Hi I am having trouble setting up the comms for the pv600 plus. I have ML1100 connected to a switch. The pv is also connected to the switch. I...
Replies
1
Views
2,841
I'm a beginner to PLC and Hmi programming. any one please help how to connect HMI to pc. HMI has a printer **** enabled by default, It does not...
Replies
5
Views
424
Hello, I've recently tried to upgrade my PLC controller from a L72 to L84ES and everything seemed to work, all buttons and screens as far...
Replies
9
Views
2,629
I imported the pva into Factory Talk View Studio and it gave me some errors. Alarm message Ack option not supported. Blinking color images are...
Replies
3
Views
1,787
I'm trying to set the date and time on a Panelview 600 plus 2711P-T6M20D8 SER A. I looked for a white square to pop up in the lower left...
Replies
6
Views
1,794
Back
Top Bottom