A customer of us wants to add a earth leakage protection (max 400mA) device in de power supply of my control cabinet. This cabinet houses several frequency converters.
What I know so far: earth leakage of Danfoss VLT2800 drivers is >3.5mA. SEW tells me the same but they make a note that the earth leakage current is also depending on motor cable length and other factors. They tell me a typical earth leakage current will be approx 25mA.
There are RFI filters available in "low leakage" style. But they limit the cable length to a maximum off 10mtr. Then I need to install motor filters as well to allow for longer motor cables.
Some manuals of frequency inverters also make note the the Inrush current of the RFI capacitor in the drive is a lot higher. (And might trip the earth leakage protection).
What is youre experience with this?
In my opinion it is not possible to connect a large (10 or more VFD in one panel) industrial control cabinet behind a 400mA earth leakage current protection. But my customer is demanding that my cabinet can be connected behind this device...
At the moment I'm not able to find solutions for this, do you know any solutions?
A customer of us wants to add a earth leakage protection (max 400mA) device in de power supply of my control cabinet. This cabinet houses several frequency converters.
What I know so far: earth leakage of Danfoss VLT2800 drivers is >3.5mA. SEW tells me the same but they make a note that the earth leakage current is also depending on motor cable length and other factors. They tell me a typical earth leakage current will be approx 25mA.
There are RFI filters available in "low leakage" style. But they limit the cable length to a maximum off 10mtr. Then I need to install motor filters as well to allow for longer motor cables.
Some manuals of frequency inverters also make note the the Inrush current of the RFI capacitor in the drive is a lot higher. (And might trip the earth leakage protection).
What is youre experience with this?
In my opinion it is not possible to connect a large (10 or more VFD in one panel) industrial control cabinet behind a 400mA earth leakage current protection. But my customer is demanding that my cabinet can be connected behind this device...
At the moment I'm not able to find solutions for this, do you know any solutions?