How Many pid loops is a compact logix processor good for?

I do not have my specific model info at the moment but what i mean is do you guy's typically use them to the max that they support?

I Have been told that using the max amount of loops is very hard on the processor and worse with other logic running and the accuracy and speed of some or all loops suffer.

Is this true? What is a good limit to leave unused and add an additional processor in general?
 
As many as memory and scan time permits. There are no other hardware limits.

I don't know about the effect of scan time, running the max, as one CompactLogix could probably support every single PID used in this plant, but that would be silly.

What model CompactLogix?

The document (included in your RSLogix Installation folder) "Execution_Time_And_Memory.pdf" lists the worst case execution time for a PID on a CompactLogix as 530.0 microseconds, on an L30, running ISA Independent mode.
 
Last edited:

Similar Topics

Hello all! First official post here... have been using the site for help but managed to find existing threads to help with all previous issues...
Replies
8
Views
1,199
Hello. I am trying to figure out how to setup a PID in Control Logix 1769 Controller in a way that it would control a drive speed by sending...
Replies
3
Views
1,610
Have a application I have been working on today using a compact logix to control temperature of molds. I am using a PID to get the Preset values...
Replies
1
Views
1,831
Have some machines that i used a micrologix 1400 plc and using thermocouple inputs and outputs to control solid state relays to maintain the...
Replies
2
Views
3,650
If anyone could help it would be appreicated....Thanks....
Replies
0
Views
2,748
Back
Top Bottom