Hi! I'm having problems getting the comms set up right! I have a PV550 2711-K5A20 and a ControlLogix5561 talking through a 1756-ENBT card. the error message on the HMI reads;

634 Read Error

IP: 192.1.1.2, Path:1 0 SRV: 1 CLS:0 INST: , ERR: 5

My comms card has the IP: 192.1.1.2 and sits in slot 1 of the rack.
The Plc is in slot 0
The panelview has the IP: 192.1.1.5 and is connected through a hub/switch to the system.

Anybody got any suggestions??
 
634 Read Fail

a> Comm Status - ControlLogix Tag or address does not exist or is the wrong data type - Check tag address / Check for data type mismatch.

b> Designated slot does not contain a ControlLogix Processor - Verify ControlLogix slot location

Suggest a> is your most likely problem - incorrect Tag address or data-type
 

Similar Topics

I have a Control Logix 5561 with a 1756-ENBT/A card and I need to communicate with a PV550. Panelbuilder help says I need a 1756-ENBT/B, does...
Replies
5
Views
1,815
I had a quick question about how to setup a button I'm adding to our existing pv-550... What I'd like to do: 1. When the button is depressed...
Replies
7
Views
4,998
Is there a way to add a stop to the attached program? I want to stop it after the first rinse so the operator would have to push a button for it...
Replies
10
Views
1,220
I'm trying to connect a PV550 (2711-T5A2L) to a 1761-NET-AIC using a 1747-C11 cable (w/RJ45 removed) and the Phoenix connector. Can someone tell...
Replies
8
Views
2,661
We have an old machine that has been mothballed since early 2018 and management are looking at more work for it in 2022. The system runs on an SLC...
Replies
12
Views
2,853
Back
Top Bottom