jcraft
Member
We have a machine that has two separate ovens on it. Both ovens have a separate thermocouple that goes back to a thermocouple card in a GE 90-30 rack. Within the GE program, thee is a single PID loop that controls the burner motor within the oven. Machine/program has been in place for 5-6 years running 24/5 so there is no issues with the programming portion up until the other day. Looking at the data trend for the oven temps ( PV,SP and CV)on the HMI it seems that at one point the system was running fine and then all of a sudden the PV (thermocouple)value locks up at one value on both ovens and stays there. The one oven it locked up below setpoint so over the next half hour you can see the the CV steadily increased to 100% ( it was gradual increase over that amount of time)until the oven was damaged and someone shut it down. AT the same time, the other oven PV value locked up at a value just below setpoint so luckily this one the CV decreased steadily. Any thoughts as to why this would happen. Could it just be a program glitch or could the card be going. Unfortunately we weren't able to monitor on-line while it was happening. Thanks