Dear Friends;
I have been working for designing an HMI in RS View32 Works and need some help for the following;
1) RS Logics sends a value 0-350 (Machine speed) in an integer N7:32 which I created a tag in Rs View. I want that whenever the value of N7:32 <= 2, Rs View log that time in a memory tag.
2) When the value of N7:32 > 2 system again log the time.

I mean whenever machine stop and start again, system log the time.
 
All you have to do is set up alarming for N7:32 and to do that you have to do the following:
In the Tag Database select N7:32 and check the box beside "Alarm" and in the pop-up configuration box set one Threshold as 2 and check Increasing and the other as 3 and check Decreasing.Give appropriate Labels.
This will cause the instances that are of interest to you get logged in a DBF file in the ACTLOG folder of your project.You can also view this logged data on your HMI screen by selecting the Alarm Summary Table available in the Library
 

Similar Topics

Dear Friends, I want to change the value of a Memory tag 3-4 times/second in RS View 32 Works. The “Pause” command in Macro can provide delay...
Replies
2
Views
2,822
Hi; To get communication with Lenze 9300 drives, we have arranged “PC System Bus Adapter” Type EMF2177IB. We have installed software “Easy...
Replies
3
Views
3,615
Hi; I had designed an HMI in RS View32 Works and an SLC-5/05 had connected with that HMI via direct driver. Now as per requirement, i need to...
Replies
4
Views
2,773
Hi; I have arranged Allen Bradley cable and adapter for communication between Laptop and Power Flex drives which picture is attached. I did try...
Replies
5
Views
2,328
Hello; In one of our Chinese flexo machine, there is a Chinese made PLC, brand "XINJE" Model XC5-48R-E. We have its programming software but all...
Replies
5
Views
2,019
Back
Top Bottom