783
hi good people, i have been asked to look at a motorized valve which is controlled by a temperture controller, the valve has a 24v to the motor all the time and the output of the temp/controller connects up to the 10v or 20ma it can do both( only one is used) so the temp controller modulates the valve? what i am after is the contoller has been changed but it is different it is a relay output how can i covert 24v to 0-10v or 0-20ma so i can use the relay controller? thanks stu
 
Sometimes it's possible to drive a motorized valve with pulses forward or reverse instead of using an analog signal. The controller in this case would have two pulse outputs.
Is your controller like that or is it one with only one relay output?
If it's not the former then you may have to purchase a different type.
Roy
 
Not going to happen with a relay output. That's probably a controller designed for electric heaters not a proportional valve. Invest in the correct controller.
 
Using the on/off output signal from the new controller will turn the proportional valve into an on/off (open/close) valve,
but maybe that's the whole idea?
Code:
controller
24V output -----
               |
              [ ] resistor
              [ ] 1.2k
              [ ] 1/2W
               |
               ------ to analog input 0-10V
               |
              [ ] resistor
              [ ] 1k
              [ ] 1/2W
               |
    ground ----------
You can use a smaller value for the bottom resistor to suit your needs: The valve will open less when controller output is on.
 

Similar Topics

Got a new piece of equipment that has a flow switch on it. But the flow switch is 4-20ma output and we don't have any analog inputs left and the...
Replies
19
Views
5,158
Hello all, I'm currently working on a servo motor linear positioning system (ball screw). I'm all set up regarding communication between my HMI...
Replies
1
Views
90
I have an application using an incremental encoder and then I convert it to degree (0-360) using calculation program. For a while, the calculation...
Replies
7
Views
242
Hi all. Me again still learning Rockwell. So I'll be polling an INT data array from a Modbus SE power meter with a L82 (with a Modbus ProSoft in...
Replies
56
Views
1,384
Hello, could someone kindly convert the attached RSP files that are currently used for SLC 5 PLC into PDF please
Replies
6
Views
528
Back
Top Bottom