I am designing a 24vdc control that does not utilize a PLC. I am thinking about running the 230V line straight to the input side of a SOLA DC power supply (SDN4-24-100LP). The machine has one 2HP, 3PH ac motor, which I will control with a VFD.In the pass I have always isolated the control voltage power supplys with an isolation transformer. Since there is no PLC an minimal electronics, I was thinking of removing the isolation transformer. Not sure if the Power Supply itself would provide enough isolation. Just trying to get opions and thoughts.
 
That supply is a small switcher. It isolated internally. No need for an isolation transformer. I can't remember a SMPS supply where I didn't see isolation. It's inherent in the design.
 
I took a look at the spreadsheet for this unit.
http://www.sola-hevi-duty.com/products/powersupplies/devicenet.htm
It meets Class 1, Div 2 isolation as it stands.
I can't see a reason you should be concerned with removing the isolation transformer.

Class 1, Div 2 has absolutely no bearing on the OP's question.

A Class I Hazardous Location is one in which flammable gases or vapors may be present in the air in sufficient quantities to be explosive or ignitable.

Div 1 means it is a location where these flammable gases/vapors are normally present under normal operating conditions. Div 2 means that those gases/vapors ~may~ be present in an abnormal (i.e., breakdown) situation.
 
Sola, Puls, and AB all make power supplies that have 480 VAC as the supply voltage. I use these in a lot of cabinets where I really don't need 120VAC and therefore don't need another transformer.
 

Similar Topics

Can an AOP be removed from Logix? I seem to have some version weirdness from an E&H AOP and I need to see if reinstalling the AOP will correct it.
Replies
5
Views
970
I'm making a meal of this, my brain's not in gear. Also, I'm new to S7 TIA/WinCC so excuse my ignorance... See redacted pic. Pressing F7 (SAVE...
Replies
10
Views
3,218
So I have a form email saying they are removing VFD support from standard TechConnect agreement and it will be an adder in the future. We have...
Replies
17
Views
12,680
Does anyone know how to calculate the savings from now needing to run an air compressor all day? Basically I have a design that replaced 6 * 1"...
Replies
26
Views
4,823
Hi all, I'm installing FTView Studio ME v11 on a Virtual Machine. Using VMWare Workstation running Windows 10 (latest updates). The installation...
Replies
3
Views
3,358
Back
Top Bottom