Help require for programming in RS View 32 works

AB2005

Member
Join Date
Nov 2006
Location
Lahore
Posts
318
Dear Friends,

I want to change the value of a Memory tag 3-4 times/second in RS View 32 Works. The “Pause” command in Macro can provide delay for only 1sec. Can anyone help me out how can I achieve that goal?
 
To achieve this goal the SCADA is not the right place to put something that needs changed often, it needs to be inside the PLC, and the trigger to make all these changes could come from the RSView.
In most cases a memory tag is a fixed value or is seldom changed unless it is a derived value that is the result of two or more values coming in from a PLC.

A one second turn around, or full scan on a scada, is probably considered to be fairly fast, and for reliability in most cases more than adequate.

You need to provide us with more information if you feel it must be done from RSView.
 
Thanks;

I have tried to achieve that goal by using System tag "System/blinkFast" in "Drived tags" and succeeded.
 

Similar Topics

Dear Friends; I have been working for designing an HMI in RS View32 Works and need some help for the following; 1) RS Logics sends a value...
Replies
1
Views
1,842
Hi; To get communication with Lenze 9300 drives, we have arranged “PC System Bus Adapter” Type EMF2177IB. We have installed software “Easy...
Replies
3
Views
3,610
Hi; I had designed an HMI in RS View32 Works and an SLC-5/05 had connected with that HMI via direct driver. Now as per requirement, i need to...
Replies
4
Views
2,771
Hi; I have arranged Allen Bradley cable and adapter for communication between Laptop and Power Flex drives which picture is attached. I did try...
Replies
5
Views
2,318
Hello; In one of our Chinese flexo machine, there is a Chinese made PLC, brand "XINJE" Model XC5-48R-E. We have its programming software but all...
Replies
5
Views
2,014
Back
Top Bottom