S7 Analogue values not steady

siamak

Member
Join Date
Sep 2009
Location
London
Posts
2
Hi everyone,

This is my first thread after joining here. so not sure about the search option if there is any, I actually preferred to start a new thread on my issue;

The analogue inputs on the OPC Scout (and therefore on the other OPC clinets) does not stay on a steady value whilst the analogue voltage on the input is steady, why that can be?

Sia
 
I'm not 100% sure as it has been a while, but on the 300 series Siemens analog input cards, we had to jumper the commons to terminal 11 to keep the values steady, and in some cases to make them work at all.

Like I said it has been a while and I can't remember if this was for two or four wire devices.

Hope this helps.
 
It is called "noise".
With an analog meter, the signal may appear to be steady, but in reality noise enters the signal path in some way.
Grounding one side is quite common.
Shorting unused channels is also quite common.
Also check if the ground is good enough.
Are your analog cables screened ?
Check if the screen is properly connected to ground.
Are there noise-generating equipment such as VFDs nearby ?
Does cables run in parralel with VFD cables ?
Is the main supply noise-free ?
etc etc.
 
well as far as noise is of concern, I have no VFD around, and even osciliscope does not show such fluctuation, but I take your replies as there is no particular arrangment apart from the standard care, I'll try and see... thanks anyway...

Particular care related commnets would be welcome.

Sia
 

Similar Topics

Hopefully an easy one. In my program I am reading my analogue input values, low engineering values and high engineering values. My analogue input...
Replies
9
Views
5,282
Guys, I have an application using FactoryTalk ME version 7. The application has been running fine for a few weeks now. I made a change today...
Replies
6
Views
2,579
Good Day Gents....New here Does anyone know if using a SLC500 and a 1746-NO4I you can associate the output value directly with the integer value...
Replies
6
Views
1,725
Hi, I received the copy of the program that is currenlty downloaded to GE90-30 CPU363. I have setup the offline system in the office with same...
Replies
3
Views
2,039
Hi New to this Can anybody help me i am trying to export live Analogue values from a LOGIX500 program to a Excel Spreadsheet and need a idiots...
Replies
2
Views
3,715
Back
Top Bottom