We have a S7 416-3XL00-OABO CPU . We are using Profibus to
communicate to SEW Drives , Fanuc Robots ,Encoders, HMI's , etc. Last evening we had a problem with 6 devices that came
off of a Siemens 6ES7-972-OAAO Repeater ( may not be the whole
number) It was 3 Fanuc Robots ( 2 RJ 2's and 1 RJ 3 ), 2 encoders , and a Siemens HMI. The CPU faulted with a EXTF Led
and IFM1F Led. We replaced the Repeater because we had a weak
DP2 Amber Led light on the repeater. When taking the wires off ,the tech took notice that one of the Profibus wires seemed broken ,they are solid wire. We replaced the repeater
but still were not able to clear the fault ,or the 6 devices
on that part of the network. Just to see if we could cut that portion of the network in half ,on the Fanuc Robot we pushed
the terminating resister in the up position (or Down)it still did not reconize the "Nodes" ,but when we put the terminating resister back to the previous position ,the fault went away.
Late today we had some random faults with the same section of the network ,we thought we had it solved.
We have had this machine for almost 9 years,and never had Profibus issues ,so the installation is sound.A few questions.
- Have any of you had similar problems?
- Would you have any ideas what could be happening?
- It is somewhat of a rough enviroment, but have been very
stable for years. We checked all the cables going to the
devices in question ,they do not look damaged.
Thank You so much in advance,
communicate to SEW Drives , Fanuc Robots ,Encoders, HMI's , etc. Last evening we had a problem with 6 devices that came
off of a Siemens 6ES7-972-OAAO Repeater ( may not be the whole
number) It was 3 Fanuc Robots ( 2 RJ 2's and 1 RJ 3 ), 2 encoders , and a Siemens HMI. The CPU faulted with a EXTF Led
and IFM1F Led. We replaced the Repeater because we had a weak
DP2 Amber Led light on the repeater. When taking the wires off ,the tech took notice that one of the Profibus wires seemed broken ,they are solid wire. We replaced the repeater
but still were not able to clear the fault ,or the 6 devices
on that part of the network. Just to see if we could cut that portion of the network in half ,on the Fanuc Robot we pushed
the terminating resister in the up position (or Down)it still did not reconize the "Nodes" ,but when we put the terminating resister back to the previous position ,the fault went away.
Late today we had some random faults with the same section of the network ,we thought we had it solved.
We have had this machine for almost 9 years,and never had Profibus issues ,so the installation is sound.A few questions.
- Have any of you had similar problems?
- Would you have any ideas what could be happening?
- It is somewhat of a rough enviroment, but have been very
stable for years. We checked all the cables going to the
devices in question ,they do not look damaged.
Thank You so much in advance,