I have unsuccessfully tried to add a new ControlNet node to an existing network.
This particular network - named our "SCADA" network - connects a few ControlLogix PLCs to dual Cimplicity SCADA servers. This is obviously mainly for SCADA display, although there is a small amount of produced and consumed tags used between a few of the PLCs.
This network has worked fine, and remains so. However, when running RSNetworx connected to the new PLCs, the rest of the network is visible, except for the SCADA servers. When running RSNetworx from other PLCs on the network, all nodes are visible, but the new Primary PLC node intermittently drops in and out, thus preventing scheduling - the secondary PLC node remains visible.
Interestingly, if the new PLC is connected solely to the SCADA nodes, that network can be scheduled and works properly.
The existing CNBR cards are series D rev 5.50 (CPUs 1756-L55 rev 13.53), whereas the new PLC's CNBR cards are series E rev 11.3 (CPUs 1756-L63 rev 15.60). Could it be a firmware issue?
Also I have noticed that there is a jump in node addresses: the nearest node is 15; our new PLC is 20. Could this cause a problem? I should add that the SMax and UMax are set appropriately for these addresses.
Any other ideas?
Cheers.
I have unsuccessfully tried to add a new ControlNet node to an existing network.
This particular network - named our "SCADA" network - connects a few ControlLogix PLCs to dual Cimplicity SCADA servers. This is obviously mainly for SCADA display, although there is a small amount of produced and consumed tags used between a few of the PLCs.
This network has worked fine, and remains so. However, when running RSNetworx connected to the new PLCs, the rest of the network is visible, except for the SCADA servers. When running RSNetworx from other PLCs on the network, all nodes are visible, but the new Primary PLC node intermittently drops in and out, thus preventing scheduling - the secondary PLC node remains visible.
Interestingly, if the new PLC is connected solely to the SCADA nodes, that network can be scheduled and works properly.
The existing CNBR cards are series D rev 5.50 (CPUs 1756-L55 rev 13.53), whereas the new PLC's CNBR cards are series E rev 11.3 (CPUs 1756-L63 rev 15.60). Could it be a firmware issue?
Also I have noticed that there is a jump in node addresses: the nearest node is 15; our new PLC is 20. Could this cause a problem? I should add that the SMax and UMax are set appropriately for these addresses.
Any other ideas?
Cheers.