Aviator|Chris
Member
Hi there,
I have a customer (Water Treatment) that has a DH+ network with 9 Nodes that are very busy. Each node is a Phoenix DH+ to Fibre Card and then from DH+ locally into ControlLogix DHRIO cards and then onto 9 individual Ethernet Networks. A total of around 42 seperate AB PLC's on site.
(PLC-DH+FibreCard-FibreRing-DH+FibreCard-PLC)
The Control Room PLC (SLC500) pulls data via MSG instructions (30 individual messages in total) from each of the main nodes.
There has been some reports that the network is running slowly of late and as the site is having most of its large treatment plants upgraded and more data brought to the Control Room, I feel this might be the root cause.
So what I was hoping to find out from this post is, how can I arrange the cascading message instructions so that there are less message connections occuring all at once? I have attached a PDF of the message sequencing method currently used.
Instead I would like to keep active connections to a limit to create more overhead on the DH+.
Any help greatly appreciated.
Cheers.
I have a customer (Water Treatment) that has a DH+ network with 9 Nodes that are very busy. Each node is a Phoenix DH+ to Fibre Card and then from DH+ locally into ControlLogix DHRIO cards and then onto 9 individual Ethernet Networks. A total of around 42 seperate AB PLC's on site.
(PLC-DH+FibreCard-FibreRing-DH+FibreCard-PLC)
The Control Room PLC (SLC500) pulls data via MSG instructions (30 individual messages in total) from each of the main nodes.
There has been some reports that the network is running slowly of late and as the site is having most of its large treatment plants upgraded and more data brought to the Control Room, I feel this might be the root cause.
So what I was hoping to find out from this post is, how can I arrange the cascading message instructions so that there are less message connections occuring all at once? I have attached a PDF of the message sequencing method currently used.
Instead I would like to keep active connections to a limit to create more overhead on the DH+.
Any help greatly appreciated.
Cheers.