SLC5/05 problem

ABDELAAL

Member
Join Date
Dec 2007
Location
ALEX.
Posts
32
Dear All,

I'm Trying to connect a PV1000 to SLC5/05 Through Ethernet .I've set up the Ethernet in both the PLC and the PV1000.These are images for the configuration.I've plugged a Reverse Ethernet cable once and direct one another time . No response of each of them. The status of the op and the plc when connecting the reverse cable is the green led is steady in both of them but no data transfer between them ,the panel says can't read the tags nor write to them. but the missing connection message disappeared.
as far as i know the physical connection between them is all right,because the two green leds are steady ,but no data transfer.
Please help me to debug if there is any error .I don't know what am i missing???????!!



Regards
 
For a direct connection, the crossover cable is required. If you use a hub or switch, use straight cables.

Your screenshots show everything set up correctly for the ethernet settings. Can you post the .rss file and the .pba files?

Perhaps there is something wrong with your tag names?
 

Similar Topics

I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
Replies
14
Views
2,551
I am trying to connect to SLC5/03 using an FTDI usb to rs232 with female to female converter at 1 end... however I can not connect to it ... the...
Replies
8
Views
1,269
Dear All, I wanna get the data from ind331 indicator(Mettler toledo) to SLC 5/05 CPU via Ethernet Ip using EEM instruction. The CPU=1747-L553...
Replies
2
Views
2,157
Hi, I want to communicate slc5/03 cpu with Delta tp04 hmi through rs232 port. I tried through 1747cp3 cable directly but can not communicate...
Replies
0
Views
932
Sorry to bother everyone but I'm having real problems. The setup is: SLC5/03 with a 1747-ASB series B in slot 1. 1794-ASB series E in the field...
Replies
14
Views
2,139
Back
Top Bottom