I am new in the PLC programming stuff and I am working with an AB PLC Logix5000 series. I am trying to access the diagnostics of the ControlNet module through a cip message in order to monitor some alarms in case of a network problem. I have found some references up to now but they dont seem to work..Please see the attached picture for the configuration of my MSG command (the path is to the CNet module). The fault that I get is '16#005 no connection' and ' wrong class or attribute'. In the source tag I have set the 0000000400 in a Dint and 02 in an INT. Any help is appreciated. Thanks
moz-screenshot.png
. In addition is there a similar way to get diagnostics for the PLC processor in case of a fault?

Untitled.jpg
 
Last edited:
See my attachment for the correct MSG setting, Source Element not needed. Then make sure the destination need to be an SINT (Short Integer) array with 6 element. And lastly your path pointed correctly to the correct ControlNet module.

50827-01.gif 50827-02.gif 50827-03.gif
 
Hi there

Thanks for the quick reply. Although the cip is now connected I still cannot see how to get diagnostics from these attributes..First of all, in the attached pic you can see the values that I have when online with healthy net. If I disconnect one Cnet tap I still have the same values alhtough there is a network error..Moreover can I find a reference of what is the attribute that each SINT looks at?

Untitled.jpg
 

Similar Topics

The application was working in Twincat 4022.16 Used VM for offline. recently changed the laptop and the getting the error with Message as below...
Replies
0
Views
52
We are using wincc scada WinCC system software V7.5 SP2 , connected to few plc . Past 3 weeks we getting this alarm continously when we checked...
Replies
0
Views
79
I am very, very new to PLCs. I only have experience with Picos, but I knew enough to save this from the dumpster. Apparently, everything on it is...
Replies
13
Views
600
Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
Replies
18
Views
1,387
Good morning guys; Im new at AB plc, and i just need help about a table or a list called something like "exchange data table" in French it is...
Replies
4
Views
765
Back
Top Bottom