Hazardous Area Question

Chado613

Member
Join Date
Mar 2005
Location
Kingston
Posts
79
Does anyone know if using Blue wireway on a control panel for wiring going to a class 1 div 1 area is required?

How about a class 1 div 2 area?

I cant find anything about this in the CSA. Im wondering if it is just good practice and not required?

Thanks
 
What is blue wireway? EMT rigid or??

I have only seen hazardous ie Class 1 div 1 or 2 done with rigid or with approved adapters for SO and other flex cord

Dan Bentler
 
Yes sorry, the above link is what I mean.

I am talking only about conductors leaving a control panel going into the field
 
It is typical to use blue for I.S. wireway and conduit. Which I presume you mean I.S., a type of wiring method (there are other's) for Class I, Division 1 area.

It's not typical for XP wiring in a Class I Division 1 area.

AFAIK, there is no NEC Code requirement. It may be mentioned in UL508.

Google "intrinsically safe blue" and you'll get some more information.
 
I was not specifically refering to I.S. or Non-incendive. I am aware of other wiring methods.

My question just was if blue wire way (panduit, wire duct, wire trough) was a requirement for any Class 1 area.

I do think you helped answer my question "AFAIK, there is no NEC Code requirement"

Thank you the Dave2
 
Yes sorry, the above link is what I mean.

I am talking only about conductors leaving a control panel going into the field

The vagueness of this is giving me fits. When you say conductor what are you talking about 240 480 4160 or low voltage signal or communication.

If you have intrinsically safe which is approved for the area you can have it sitting out in the open and run intrinsically safe conductors / cable however you want - almost. you avoid having to put it in conduit.

Check your equipment listing and the connecting cable and make sure all is intrinsically safe. If not you will probably have ot use a conduit or cable system that complies with NEC (or CSA in your case) hazardous area requirements.

Dan Bentler
 
I have never seen a Code that spells out the blue panduit. It is however an industry standard. What that means is in certain industries (Chemical is main one) it is expected. Do a google search on NAMUR. It is an internatinal standard and you will see the blue panduit and wires refered to there.

We do some work were our customers request this standard. Personnaly I think it is a good standard
 
The vagueness of this is giving me fits. When you say conductor what are you talking about 240 480 4160 or low voltage signal or communication.

If you have intrinsically safe which is approved for the area you can have it sitting out in the open and run intrinsically safe conductors / cable however you want - almost. you avoid having to put it in conduit.

Check your equipment listing and the connecting cable and make sure all is intrinsically safe. If not you will probably have ot use a conduit or cable system that complies with NEC (or CSA in your case) hazardous area requirements.

Dan Bentler

The conductors I mentioned before coming from the Control Panel, could be 120VAC, 24VDC, or network it doesnt matter.

I apprecaite the information you provided but doesnt have anything to do with my original question.
 
I have never seen a Code that spells out the blue panduit. It is however an industry standard. What that means is in certain industries (Chemical is main one) it is expected. Do a google search on NAMUR. It is an internatinal standard and you will see the blue panduit and wires refered to there.

We do some work were our customers request this standard. Personnaly I think it is a good standard


Thank you this was very helpful
 
No, it's not a requirement, blue wireway and blue jacketed cable is just a way of distinguishing between Intrinsic Safe and Non Intrinsic Safe wiring. I don't believe it's mandated just common practice.
Roy
 
hazardous location

Class one Div 1 is now called class 1 zone 1. Intrinsically safe is labeled as (i), (ia) , (ib).
Flame proof = (d)
increased safety = (e)
oil immersed = (o)
pressurized = (p)
etc etc..All equipment must be labeled for its application. Read section 18-066 of the code. Appendix B and appendix F. Also there may be amendments for your province.
 

Similar Topics

In the U.S. under the current standards is it allowable to use a friction brake for tension control in a hazardous area with a Group D gas with an...
Replies
11
Views
3,919
Looking for a way to monitor humidity in a Class 1 Div 2 area using wireless, battery powered, and a laptop to log data. Any recommendations? I...
Replies
9
Views
2,735
I'm looking for an electrical enclosure heater that is rated Class 1 div. 2. Need to keep the electronics inside above 0 degc. I don't have the...
Replies
1
Views
3,247
I am looking to place moveable operator stations in our production rooms. These rooms are classified as a Class 1 Div 2 or Zone 2 area. These...
Replies
7
Views
3,606
What is meant by Hazardous area classification for PLCs ? What is Class and Div ? Do any Safety PLCs comply with these Class and Div ? What about...
Replies
6
Views
4,169
Back
Top Bottom