Hi everyone
I’m beginner and I have a strange problem with wincc flexible.
There is a kind of valve in the project that sends 2 bit for its status:
“open_status” and “close_status”.

So I there are 4 conditions:

- close status = 0 and open_status= 1 : valve is open
- close status = 1 and open_status= 0 : valve is closed
- close status = 0 and open_status= 0 : valve fault
- close status = 1 and open_status= 1 : valve fault

I want to show status of a valve with a graphic object in different colors.
I make an integer tag: “valve_status”.
On “Change value” of two bits (“open_status” and “close_status”), there is a script to check 2 bits and update “valve_status” with the new number:

- close status = 0 and open_status= 1 : valve_status = 1 valve is open
- close status = 1 and open_status= 0 : valve_status = 0 valve is closed
- close status = 0 and open_status= 0 : valve_status = 2 valve fault
- close status = 1 and open_status= 1 : valve_status = 2 valve fault

I assign “valve_status” to appearance of the graphic object and give it 3 different colors.
The problem is that it works in simulator without any problem, but it doesn’t work in real OP.
The script doesn’t run in real OP. In fact I place 2 graphic objects in the screen and assign two bits (open and close status) to them. It makes the problem gone! But it’s not good.

I’m sorry for explaining too much!
Any idea!?
 
I make an integer tag: “valve_status”.
In fact I place 2 graphic objects in the screen and assign two bits (open and close status) to them.
The problem could be that you may actually be using a binary tag for your Valve_Status, which can only have 2 values (not 3 as you need).
 
(rant alert)

I cringe when I see people jumping to using scripts for anything.
There ought to be a big fat warning in WinCC Flexible, telling users to not use scripts unless there is no other way, and then only very sparingly.

(rant finished)

Use the PLC to pack the animation tag based on the sensors. Dont use the HMI for this.
Then use appearance animation that are linked to the animation tag to achieve what you want.
 

Similar Topics

I have wincc flex 2008 project made with wincc flexible 2088 sp1 project hmi device is simatic pc panel 19" I want to change hmi device to run the...
Replies
17
Views
5,275
Dear All, i want to know how we Date and Time set and Change from HMI MP277 use Wincc Flexible.PLC is S7 300 CPU 315 2-DP.i use SFC0,SFC1 but...
Replies
4
Views
5,713
In my project, I have 2 CPU which are A and B. Recently, I need to configure the WinCC Flexible to finding the Master CPU for change connection...
Replies
7
Views
5,811
Hi, We have upgraded our laptop which includes Windows 11. It appears that WinCC flexible 2008 advanced does not support Windows 11. What...
Replies
11
Views
264
Hello everyone I Have an Issue with the usage of recipes in Wincc Flexible 2008, I create the recipe to change the values in a fast way The...
Replies
0
Views
103
Back
Top Bottom