hi guys, i am trying to set up some alarms on the screen when an e/stop is pressed or if a timer has timed out ? what is the best way to do this? i am using factory talk studio. thanks for your time, stu
I use an integer to drive alarms on the PV.
If Current_alarm=1, display message associated with value of 1.
If Current_alarm=2, display message associated with value 2 and so on.
Map each of the alarms in the PLC to the same Ineteger register (Current_Alarm).
1=E-stop PB
2=Generic Alarm
3=Some other alarm
and so on.
Use the Alarm Banner to display the current alarm.
Or, you could use the Alarm History banner.
Up to you.
When setting up the Alarm Banner, use the "Value" for the trigger (which will be your Current_alarm register).
When resetting the existing Alarms, MOV a "0" to the Current_Alarm register.
It clears the exisitng alarms, and the Alarm Banner disappears from the PV screen, unless there's an active alarm in which case it will show up again.
You may try to latch alarms and display or rotate messages for multiple existing alarms.
Hope this helps.