i'm using controllogix-5000 plc and using MODBUS to read and write data to external DCS.(USING MVI56-MNET)
Now the problem is that upto PLC all the data are ok, but after modbus,most data are fluctuating(HUNTING) in DCS.
all analog data having variation in DCS.
can anyone suggest me what will be the reason and its solution?
 
Is the data hunting or dropping out. I have had Modbus installations where comm issues like noise and timing has cause the comms to drop out and look like it is hunting.

Once the data is digital it does not change like analog signals can when there is noise or a ground loop. With digital comms it works or it doesn't. If the data is fluctuating like hunting it could be also be caused by a configuration error where different data is being written to the same location. This would cause different numbers to be showing up in a register.
 

Similar Topics

Hi, I'm having some issues getting my PLC to talk with a meter and genset controller over Modbus. The PLC is a ControlLogix 5572 with 2 Prosoft...
Replies
4
Views
4,716
I am having difficulties setting up MVI56E-MNET card to send and receive data from/to my touch screen via Controllogix 1756-L73S processor. Info...
Replies
7
Views
2,603
Hi How to customize the address mapping in MVI56-MNET with RSlogix 5000. i have 10001 to 10064 digital status and 30001 to 30107 analog status.
Replies
0
Views
1,773
Guys I have a project where I'll be required to exchange data with an upstream PLC( Schnider) over Modbus/TCP/IP. On my side I'm using a...
Replies
12
Views
11,728
Good day guys. I have a third party device with its Modbus registers which I want to copy/set up on a plc because I need to convert my Modbus tcp...
Replies
3
Views
112
Back
Top Bottom