Can anyone tell me the right configuration to connect to a SLC 5-05(i.e. cable,driver)? It uses a Advanced Interface Convertor(AIC) cat. no.1761-NET-AIC. and I have not seen this before. Not that I have seen alot! Thank you in advanced for your help. :)
 
If you have a laptop with an ethernet connection the cheapest option would be to use a cross-over cable and connect directly to the ethernet port.

Darren
 
Carbonboy,

are you sure that it is an SLC5/05 ?
The AIC is used for DH485 type of network.

The SLC5/05 CPU has an Ethernet port (ch1) and a serial port (ch0).
The SLC5/03 CPU has a DH485 port (ch1) and a serial port (ch0).

It is possible to set up the serial port on either model to use the DH485 protocol, but it is most common to use the DF1 protocol.

If ch0 is set up for DF1 protocol, all you need for programming your SLC5/05 or SLC5/03 is a 9-pin nullmodem cable.
Description of cable:
pin 5 to pin 5
pin 2 to pin 3
pin 3 to pin 2

Of course, if you do have an SLC5/05, then you can also connect to it via ethernet.
 

Similar Topics

I am trying to use pylogix to write to a string array ID_Data_Table_Name. In the array there are 200 possible entries. For...
Replies
13
Views
4,017
Hey guys, I have a client that has a v-notch chlorinator that doesn't run off a 4-20mA loop, it instead has two discrete inputs that drive the...
Replies
6
Views
1,856
Hey all. I need some guidance here. This is something I came across today when a Ref guy noticed that the HMI isn't displaying the correct time...
Replies
2
Views
1,447
i am a beginner plc programmer and have some confusion, a little help would be appreciated . why do we use a normally close contact when we are...
Replies
11
Views
2,930
Hello everyone! So, for my job I need to use the web server of a S7-1200 for setting some variables. Thing is, since I'm not the only one using it...
Replies
1
Views
1,362
Back
Top Bottom