Frequency Sampling

BeetleBailey

Member
Join Date
Nov 2009
Location
Michigan
Posts
1
I am new to PLCS.Net but I am searching for what I hope is a simple solution. I have a 0-10V Pulse Output at 5-3500 Hz. I would like to measure frequency with fast response time and have the output tied directly with an Allen Bradley PLC.

Is there a simple module I can add into the PLC?

Please educate the mechanical engineer.

Thank you for your time.
 
Not knowing your hardware I would suggest a frequency transmitter that converts frequency to 4-20 mA signal. Then you can use regular analog inputs without having to use a counter module.

Frequency detection is a pain to do with a PLC especially what you want to do. Converting the signal to a standard signal is the easiest way. Use a Redlion, or Action Instruments freq to mA converter to do this. You also can find these on Omega.com.
 
There is a fast counter modules available at least for Allen-Bradley PLC, but I'm not sure what is a freq. limits. They would take you input directly. If 2 expensive - take a regular 4-20 mA module and some sort of frequency transmitter between your signal and PLC
 
It all depends on which AB PLC you're using. There are micros with counter inputs built in. If you're using a slot based processor then the frequency to 4-20ma converter is a good call especially if you've only got one frequency to measure.

Good Luck,

(8{)} :) .)
(Yosi)
 

Similar Topics

Protocol: Modbus RTU PLC: AB/Rockwell Micro850 as master The PLC is able to read and write holding registers from 20 devices. I want to...
Replies
0
Views
2,970
Hello I am having a problem with OB35 I am calling OB35 with 10Hz frequency each 10ms and sometimes PLC gives SF. What is the real limit for...
Replies
21
Views
7,069
Hello guys, I am new to this forum and have some problems with my PowerFlex755 EENET frequency inverter. I want to do a point to point...
Replies
9
Views
383
Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
Replies
6
Views
295
Communication between devices will stop working for a certain period of time. I caught the error message using WireShark. I cannot identify the...
Replies
0
Views
101
Back