ControlLogix change run to program mode delay

Carvalho

Member
Join Date
Feb 2008
Location
Setubal
Posts
10
Hello

I am working in a project where I use a processor 1756-L63, two ethernet cards 1756-ENBT/A to have a redundancy network with the supervision system and also have one module 1756-CNB/D and one 1756-DHRIO/C.
My problem is when I change the program from Run mode to Program mode appears the next message and the processor continuos in Rum mode only after 2 or 3 times try to change the mode just change.
I see and the description tell me this problem is related with the motion or message still executing.

Someone ever had this problem? How solved?

Thank you
Nuno Carvalho

moz-screenshot-2.png


error.jpg
 
Last edited:
The processor must complete or time out all communication messages before it will transition to program mode. If you have a continuous task, try increasing the communication time slice. Better yet, change the continuous task to a periodic task.
 

Similar Topics

Is it possible to dynamically change Tag Names (in real-time) on these PLCs? I'm guessing the answer is "NO", right? Just externally, then...
Replies
10
Views
3,865
Hello, Today I am trying to figure out the best way to write from controllogix to a plc5 only on change. The situation: - Migrated a Winview...
Replies
3
Views
2,109
I usually make a master program that I then use on different processes where the only difference is vessel sizes and setpoint ranges. I have the...
Replies
3
Views
2,092
Currently I use an MRP (Motion Redefine Position) to adjust position. Is there an SSV where I can directly change the absolute feedback offset...
Replies
1
Views
1,945
Hello. What is the right procedure for online change of AI module configuration parameters (input range) with redundant AI modules (over...
Replies
0
Views
2,491
Back
Top Bottom