Hi,

Apologies if this was already answered but i could not find it. I have downloaded a project to a tp177micro but with the wrong comms settings to the plc. My problem is that before i downloaded the project to the panel i set the startup delay to zero seconds and hence i cannot access the transfer mode of the panel to download new comms settings to the panel. I used usb/ppi cable to download project and wincc 2008. I have tried to restore to factory settings with prosave but have no .psb image to do so.

Any help on resetting to factory defaults would be greatly appreciated.

Regards,
Barry. o_O
 
Hi Barry

The images for the panel can be found under
C:\Program Files\Siemens\SIMATIC WinCC flexible\WinCC flexible Images
Sometimes Prosave is set to look in a different location.

edit: And you must use the OS Update function, and look for .img files not .psb files.
In order to connect to the panel upon powerup, activate the "reset to factory default", connect the panel to the PC, start the OS Update and then cycle power on the panel.
 
Last edited:
Jesper,

Many thanks for your quick reply. Worked a treat.

Hopefully someday i may be able to return the favour and help you.

Regards,
Barry
 

Similar Topics

Hi everyone, i have a Siemens S7-300 Cpu 314C-2 DP with several cards of i/o and servos my laptop has TIA version 16 and 17 loaded and...
Replies
3
Views
23
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
Replies
2
Views
30
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
26
Views
311
Hi everyone, I am an omron plc tec , lately I came across a siemens s7 200 cn plc . Can someone help me regarding the software required and...
Replies
26
Views
472
This is the first time I am working with Simatic Manager Step7 as I started my siemens journey with TIA which is pretty easy and do a lot of stuff...
Replies
3
Views
118
Back
Top Bottom