Can the modules of compactlogix be used in controllogix system?

hanachen

Member
Join Date
Nov 2009
Location
Atlanta
Posts
9
Hi
I just got a new logix5561 from Rockwell. I already had a compactlogixL43 connecting with Kinetix 6000 Servo Drive.
The problem is that there is no sercos module for the logix5561,
Is it possible I can use the module for the compactlogix? how?

Thanks a lot
 
For ControlLogix controllers such as the 1756-L61, you can use the SERCOS motion modules 1756-M03SE, -M08SE, and -M16SE.
 
For ControlLogix controllers such as the 1756-L61, you can use the SERCOS motion modules 1756-M03SE, -M08SE, and -M16SE.

Thanks for the reply.
Sorry.I might make a mistake about what I am asking.
I have the sercos module for compactlogix.
Can I plug it off and use that for the controllogix?Cause I do not have the module for controllogix.
Or is it possible I could just use the module for the compactlogix with the controllogix cntrollers?
 
Last edited:
No.

There is no adapter or connector that can interconnect the 1768 or 1769 series CompactLogix backplane to the 1756-series ControlLogix backplane.
 
Why are you moving from a CompactLogix to a ControlLogix ? Are you expanding the application, or the number of axes, or something else ?
 
The CompactLogix 1768-L45 can control up to eight axis using two SERCOS modules
Absolutely!
L45 is the way to go, you already have the hardware, just get an extra sercos card and you're good to go.
Finished a project a couple of months ago with L45 and 6 axes.
Worked like a charm.
 

Similar Topics

I have been having this error on the CPU Compactlogix L32Cwhich says that I/O are not responding . I checked in the minor faults and cleared...
Replies
6
Views
2,084
Hello all, I have a requirement to spec. a PLC system with local Safety modules. However, I'm unable to add local safety I/O modules. I have...
Replies
4
Views
1,915
My Friend is in Mexico working in an older machine, he calls me because after he did a Firmware upgrade of the processor from v20 to v24 his...
Replies
8
Views
2,287
I got this CompactLogix 1769-L33ER talking and updated firmware to V27.11. Module Discovery doesn't appear to read anything when online. So...
Replies
3
Views
1,612
Hello Currently I am using a compactlogic PLC and I am curious if there are any restrictions on using 32 point modules in the racks. I have read...
Replies
2
Views
1,623
Back
Top Bottom