Hi folks,
I am writing with request for HELP.
At our plant a request for modification of HMI project appears.
Unforunately when the compilation stars it ends with more than 350 errors.:confused:
Problem might be with some kind of driver: SIMATIC NC comunication driver
Machine has a 4 axes robot and the tags in red are for that robot.
The robot is controled by FM357-2

All errors are "INVALID DATA TYPE"
Just one error differs. It is for the driver above.

Any ideas are very much appreciated.🍺
I attached log file also. ;)

errors.png error2.jpg
 
What kind of communications driver is used ?
Post a screenshot of the connection dialog.
DOUBLE could sound as you use OPC, and then a DOUBLE is a 64-bit floating point value. Does the controller support that ?
 
Thanks for the answers and
sorry for missunderstanding.
The machine is working at the moment without problems.
We have recieved the sourse files from the producer and imediateli programmers were asked to add some buttons, messages etc.

Some variables have to be connected to NC FM357-2 also

Yes there is OPC server (I am not familiar with)

The attachments are from offline compiling.

For example
C_RP:u1,c1,1727
is register from NC program.

Have a nice weekend.
I will continieuo_O

comunication.jpg tags.jpg 351err.jpg
 
My guess is that Simatic_NC requires an option software to be added to STEP7, and you do not have this option software.
To check if it may be the problem, in STEP7, try to select the root of the project tree, right-click, select Object Properties, and go to the Required Software Packages tab. Use the button Execute to run a check.

Anyway. Since the program is not made by you, you must be very careful about changing anything in the program.
 

Similar Topics

Hi, I have been called to site after Siemens(Bangladesh) upgraded my customers OP37 Panels to MP370 Panels - since the upgrade none of the date...
Replies
2
Views
2,475
Hello All, I need urgent help.Operator panel MP370 is defetc.Not running.Program is on Flash eprom. May i load this program to my pc and run...
Replies
3
Views
1,690
Hello, I have a COMPACTLOGIX 5370 and a PV800 (2711R-T7T) in a panel. When I power cycle the panel the PV800 display boots up before the PLC and...
Replies
1
Views
1,326
I am planning on working with a cognex scanner 370 series using a beckhoff PLC and Ethernet/IP protocol. My question is does anyone know if the...
Replies
1
Views
1,234
Does anyone know how to synchronise the time between these two? I had thought that the HMI could write a LINT (time/date in microsecronds) to the...
Replies
5
Views
2,163
Back
Top Bottom