This network takes 4 bits from the PV Screen: run, jog, thread, stop and 2 analog signals: run reference & run speed. Also a Device Net Card is connected to a DC Drive.
PanelView 550 Cat. 2711-K5A2 Rev. A Frn 2.01
Connected to SLC 500 DH 485 Link Coupler
Connected to 1761-NET-AIC
Connected to SLC5/03 1747-Ls32 Ser. D Rev 4
The PLC on this small network had been powered down and the PLC lost it’s memory. Loaded the PLC memory and the equipment run about 15 minutes without problems then the PV & PLC stop communicating. However the PLC is running without errors and the I/O hardwired devices work. The PV reads “no active nodes found on Network”. Checked cables, connectors & AIC also voltages OK, checked by replacing then putting the original back. Downloaded earlier save copy of the program & have same problem.
The PV Set Up Screen: baud rate is 19200, node 2 also it shows a Flashing Comm LED and the Fault LED is out. So I believe it and the hardware is healthy. When memory was lost from power down downloaded PLC program by unplugging the PV cable from the processor. Now cannot connect serial have to connect into the 485 connector. Believe something is causing this PLC Channel to be confused. I am working for a Company that has AB, I formerly worked for a Company that had GE & Westinghouse electronics so I continue to learn about AB as I go and from this site. I always try to exhaust my own resources before asking for assistance on this site. Any ideas would be appreciated.
PanelView 550 Cat. 2711-K5A2 Rev. A Frn 2.01
Connected to SLC 500 DH 485 Link Coupler
Connected to 1761-NET-AIC
Connected to SLC5/03 1747-Ls32 Ser. D Rev 4
The PLC on this small network had been powered down and the PLC lost it’s memory. Loaded the PLC memory and the equipment run about 15 minutes without problems then the PV & PLC stop communicating. However the PLC is running without errors and the I/O hardwired devices work. The PV reads “no active nodes found on Network”. Checked cables, connectors & AIC also voltages OK, checked by replacing then putting the original back. Downloaded earlier save copy of the program & have same problem.
The PV Set Up Screen: baud rate is 19200, node 2 also it shows a Flashing Comm LED and the Fault LED is out. So I believe it and the hardware is healthy. When memory was lost from power down downloaded PLC program by unplugging the PV cable from the processor. Now cannot connect serial have to connect into the 485 connector. Believe something is causing this PLC Channel to be confused. I am working for a Company that has AB, I formerly worked for a Company that had GE & Westinghouse electronics so I continue to learn about AB as I go and from this site. I always try to exhaust my own resources before asking for assistance on this site. Any ideas would be appreciated.