We have Allen-Bradley PLC's with Relay output cards.
My question is if I'm using 24VDC from the output to drive a coil, do I use an MOV or a diode? MOV's are bi-directional and we use them on our relay outputs for driving 120Vac solenoids with some success. But I don't have much experience with DC. What is the reason for using the diode? I've found that Allen-Bradley recommends a 1N4004.

Thanks.
 
The diode protects the transistors in the output card from the high voltage that is created when the coils magnetic field collapses. Although I am not sure that it is needed using a relay output card.
 
Last edited:
If you are using relay output module, not transistors are involved into contactor coil energizing. So if contactors are not very big, you may go without any suppression.
Purpose of a diods across contactor's coil - to create a shirt sircuit and because of that to speed up drop time of the contactor. From a theory, when you removing power from any inductance, the inductance generate current which is directed in a manner to maintaine inductance. So, if you connect a diod across the coil in a way it connected in oppozit direction, the diod will minimize the selfinductance effect.
 
The diode protects the transistors in the output card from the high voltage that is created when the coils magnetic field collapses. Although I am not sure that it is needed using a relay output card.

Its considering a good design practice to use it no matter what is driving it.
 

Similar Topics

I'm not sure the best way to do this. I've got an old GE plc with only 120V relay outputs. I'm replacing a UV light component with an LED...
Replies
2
Views
1,906
Hello, I am a final year diploma student doing an automation project. Currently, I am finding how to connect an AC motor to DC PLC with relay...
Replies
16
Views
8,572
The other day, I was musing over the reliability of plc’s 10 years ago, when I first started nervously dabbling with plc programming, I put a...
Replies
1
Views
6,593
Hi looking to install a smaller less sophisticated PLC for fountain timing and also one analog pressure sensor which would be used to detect...
Replies
23
Views
614
I have a Automation Direct Click Plus that you can buy option CPU slot modules for input/outputs. The slot modules have the options of sinking...
Replies
9
Views
2,888
Back
Top Bottom