Hey Friends

I am using EZTouch PLC. I am trying to connect with a diameter gauge of 1 micron accuracy through an analog input module. The output of gauge in terms of voltage and the range is 0-10v. The resolution of analog input module is 12bit. Can i get this 1 micron change of product through this analog module????

i am a beginner and sorry ,if the question is foolish!!!!!!!!
 
IF your analog input module is unipolar (positive only), and IF your gauge maximum OD is 0.4096 cm, then yes, you can measure down to the micron level. However, the analog input will probably still experience conversion jitter, reducing accuracy.

If the analog input is bi-polar, then the maximum OD (at 10VDC) can be only 0.2048 cm.

The accuracy will also depend on the dynamic range of the analog output of the gauge head, and the calibration specifications on the input module.
 
As the 2 GURUs have state you need to provide more info on your sensor. I have tried this before with several different manufacture gauges/ sensors. I have gotten marginal at bestresults with the lower end less than $5K. The sensor needs to measure sub-micron in order for you te get a good reading. If the resolution of you sensor is +/- 2 microns then no you will never get 1 micron reading that mean anything.
 
Gauge Spec

Thank You for all
The Gauge specification is given below

Measuring axis
Single axis
Measuring gate
59mm by 59mm
Measurement range
0.2 to 50mm
Measurement error at an ambient temperature of 20C:
Object at the centre of the gate < +/-1.5micro m +/- 0.008%.
Object >0.5mm anywhere within the gate < +/-4 micro m +/- 0.016%.
Temperature coefficient of measurement
< [+/-0.05 micro m 0.001%] per degree C over the range +5 to +45 degree C.
Scan [measurement] rate
600Hz.
Measurement jitter:
Scan to scan < 6 micro m + 0.1%
Block of 8 scans to block of 8 scans < 1.5 micro m + 0.05%
Block of 80 scans to block of 80 scans < 0.7 micro m + 0.01%
FFT residual results, typical:
The results are not zero for a constant sample diameter due to measurement errors;
typical results are given below.
At a 600Hz sample rate, maximum amplitude for any frequency up to one quarter of
the sample rate = 0.6 micro m + 0.02%
At a 30Hz sample rate, maximum amplitude for any frequency up to one quarter of
the sample rate = 0.4 micro m + 0.01%
SPC residual results, typical:
The results are not zero for a constant sample diameter due to measurement errors;
typical results are given below for a 10s data collection period. Note that these are
better than the scan jitter figures would suggest because it is typical data.
With a 1mm sample: max = +0.6 micro m, min = -0.6 micro m, Sigma= 0.2 micro m
With a 30mm sample: max = +9 micro m, min = -9 micro m, Sigma = 3 micro m
 
Last edited:
The Dynamic range is there on the measurement of the gauge, but best case is still a +/- 1.5 micron error, so no, 1 micron accuracy is not possible.

However, that still doesn't give the analog output accuracies, which should probably be good. Next, is take a look at the spec sheet for your PLC analog input, INCLUDING it's sampling time.

The Input sampling time vs. the gauge's conversion time can also introduce errors, but I feel you will have the greatest error with the PLC analog input, it being a slow, low-cost one.
 

Similar Topics

Hello! I want to write PC-software for measure length of hot rail after finishing mill via analysing image made by digital camera. Could you...
Replies
3
Views
1,368
I would like to invest in high speed camera that I would use t analyse problems in high speed processes. f.i. machines with fast motion control...
Replies
8
Views
4,650
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
Replies
5
Views
62
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
5
Views
105
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
30
Views
1,111
Back
Top Bottom