Schneider System

rigicon

Member
Join Date
Aug 2009
Location
kent
Posts
415
Hi, Yet again a new system to learn from the beginning. Each customer always wants there particular brand of PLC. This new customer wants schneider. Downloaded the Twido software.
Here is the question - I have
1 x PLC TWDLCDE40DRF
7 x VFD's ATV312HV75N4
1 x HMI XBTG2220

I want to connect the plc via comms to the VFD's.
I had the PLC as master MODBUS then each VFD as slaves and the HMI as a slave. Then I wasn't sure the HMI would be a slave.
The PLC has 1 ethernet port which I was going to use for programming and a 485 for canopen or modbus there is a option for another 485 port. Should I use canopen or modbus?
Should I get the option and have 2 485 networks one for VFD's and the other for the HMI.
Any help would be much appreciated.🍻
 
You might also consider adding a switch to support programming and the HMI. I'm currently finishing up a Schneider system and the HMI works much better on ethernet verses any serial connection; in fact its painfully slow if you don't use ethernet.
 
Thanks that makes sense wasn't sure if the HMI had a ethernet port. Haven't received the bits yet. If it does I think you are 100% right.
I'll have the HMI connected to a switch with the PLC and the PC(programmer) and I'll use the 485 for the VFD's what protocol do you recommend Canopen or Modbus. I was leaning towards Modbus.
 

Similar Topics

Need your Advice. Scenario: I have got two SCADA computers at different locations which are having independent working plants at each site (But...
Replies
7
Views
2,985
Hello dear experts! I need your assistance in the following. I have a hot standby system based on Schneider Quantum CPUs with RIO nodes on Modicon...
Replies
9
Views
3,989
hi to all, have anyone tried to communicate Schneider PM800 to a ML1400 through rs485? i am having an issue with it just receiving message...
Replies
1
Views
36
Hello All, I am stumped on how to convert a %MW to a %MF using Machine Expert Basic and a Modicon M221. The help files show a word to a double...
Replies
4
Views
156
Hi, Is Control Expert V15.0 supposed to support multiple monitors? I'm running Control Expert V15.0 on my host Windows 11 PC, connected to two...
Replies
1
Views
87
Back
Top Bottom