That depends on the processor you have and how new it is, see quote below from AB knowledge.

58253 - SLC Processors that Support Modbus Protocol

Do any of the SLC processors support Modbus protocol?



In June of 2008 Series C FRN 11 was introduced for the SLC 5/03, 5/04 and 5/05 processors which added support for Modbus RTU Master capabilities on the CH0 (serial) port.
In order to support the Modbus communication capabilities RSLogix500 must be at ver 8.1 or greater.

Older processors FRN can be updated (via upgrade kit ordered from local distributors) in order to support this enhancement.
SLC5/03 upgrade kit P/N is 1747-OS302
SLC5/04 upgrade kit P/N is 1747-OS401
SLC5/05 upgrade kit P/N is 1747-DU501

Or a Prosoft module would also work.
 

Similar Topics

I thought I read somewhere the newest SLC 505s suppot modbus natively on the RS232 port. But now I cant seem to find info on it. Was I dreaming...
Replies
3
Views
3,168
Hey does anyone know whether or not SLC 505 or the Compact Logix PLC's can do Modbus TCP/IP protocol. Need to run out to a TCP/IP client from...
Replies
3
Views
4,195
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
93
Hello, I inherited a control system one of my predecessors thought it was a good idea to put logic for cant optimization and Kinetix motion...
Replies
15
Views
3,551
Probably a silly question and asked a hundred times already, but i tried to do some searching here and couldn't find this question. I have 502's...
Replies
9
Views
2,999
Back
Top Bottom