Thank you Nonuke but I'm totally missing something. I've looked at Mickey's link again and totally understand how that works with photo cells. I just don't get why we would set up a drive to source. I've got some research to do.
Thanks again
Jeff
If your PLC Output was a Sourcing type. Lets say 24VDC Sourcing, which is common. You would have to set your VFD Inputs to Sinking. If your PLC Output was a Sinking type, you would have to set your VFD Inputs to Sourcing.
Sourcing Outputs pull the voltage up to the Output Card Supply Positive Voltage (V+). Sinking Outputs pull the Output Voltage to the Output Card Supply Common or Negative (V-).
Sinking Inputs expect a Positive Input Voltage, and the Inputs Common Rail is connected to V-. Sourcing Inputs expect to be pulled to Common (V-), and the Inputs Common is connected to V+.
The most common in my experience is Sourcing Outputs and Sinking Inputs. I only use Sinking Outputs, or Sourcing Inputs, when I have no other choice due to the equipment I have to connect to.
There is usually a diagram in the VFD Manual showing the typical configuration. It basically consists of an Optoisolator for each Input with one side connected to the Input Terminal, and the other side connected to the Common Rail. Many VFDs will allow you to user either Sourcing or Sinking depending wether you connect V+ (Sourcing Input from Sinking PLC Output) or V- (Sinking Input from Sourcing PLC Output) to the Common Rail. The V+ or V- connection to the Common Rail insures that Current flows in the correct direction through the Optoisolators internal LED.
If you connect a VFD's Inputs directly to a PLC or other device. There is usually a jumper to the VFD's Internal Supply for use with Push Buttons, or Volts Free Contacts. This should be removed when the VFD is used with a PLC etc. This should be documented in the VFD's Manual.
I hope that helps clear it up some.
Stu......