slc 5/05 pid gain reset rate

Adam303

Lifetime Supporting Member
Join Date
Aug 2009
Location
Chicago
Posts
587
Hi to all. I have to access the pid setting gain,reset and rate via an hmi. gain and rest value being min. 0 and max 3276.7 and rate min.0 max. 327
Whan i enter the gain value of 5 via the hmi the accual value in the pid instructin Gain is accually 0.5 insted of 5 like i entered.
Should i multiply the value by 10???
thanks for all your help.
 
Hi to all. I have to access the pid setting gain,reset and rate via an hmi. gain and rest value being min. 0 and max 3276.7 and rate min.0 max. 327
Whan i enter the gain value of 5 via the hmi the accual value in the pid instructin Gain is accually 0.5 insted of 5 like i entered.
Should i multiply the value by 10???
thanks for all your help.
Acutually, since they are integers in the 5/05, you'll need to divide them by 10 (and 100) in the HMI scaling parameters so they are properly displayed.
 

Similar Topics

Hi everyone, yet another PID problem. I'm hoping I understand enough of the process I'm controlling that my request for help is reasonable. If a...
Replies
113
Views
27,909
How can I test some PID code I have written for a SLC-500 in RSLogix500, without having an actual processor to test on. I have used Emulate500 to...
Replies
3
Views
1,826
Hello, I have a PID block in my program controlling pump speed in order to get a correct Differential pressure. The way I have it set up is the...
Replies
3
Views
1,251
I have a PID in a SLC 500 that does not function as it should. Have deleted it remade it and still have a problem also moved it up and down in the...
Replies
13
Views
2,740
Hi all, Came across some examples today of PID instructions in an SLC 5/04 with the Setpoint (SMax) & Setpoint (SMin) both set to zero. In...
Replies
2
Views
1,915
Back
Top Bottom