I have to read the gross data from Siwarex. I actually had done it before and also have written a FB for this application which calls SFC59 RD_REC but this time we are using 315-2AG10 CPU which doesnt let me download SFC59 so how can I get gross data from Siwarex? Should I try to read PIW? If so which bytes of PIW data will give me gross? Thanks a lot.
 
Hello,
If you configure SiwarexU in base rack for I/O access:
Properties / Basic Parameters / Type of Communication: I/O Communication,
you can read current weight as word value at relative address 2.
Say, module inputs start address is 256, current weight address is 258:
(in SCL, structured text, address is in input image area)
current_weight: INT;
current_weight := WORD_TO_INT( IW258);
As current weight you get integer value from -32768 to 32767 configured weight units.
You can (have to) use Siwatool U software on PC to set (via RS232 interface) parameters of Siwarex module (scale, ...).
I hope you have Siwarex manuals, if not you can download them from Siemens site.
Hope it will help.
 

Similar Topics

Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
3
Views
43
Hi all, i have 8 CJ2m plc units that show different numbers on the plc display and i am stuck on reading the info. my unit has an ip address of...
Replies
3
Views
81
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
Replies
1
Views
81
Trying to setup a message read via Ethernet. I have the path setup as 1, 1, 2, 192.168.66.10 I get an error code 1, ext err 315. I am beating...
Replies
9
Views
231
Dear all, I don't know why setup of password became challenging and weird. After setting up the password and try to upload the ladder from the plc...
Replies
3
Views
172
Back
Top Bottom