I have been told that motors less than 100 ft. (actually 150 ft.) of wire length from the drive do not need the special cables
or output reactors, but I have also seen motors lose bearings due to VFDs when the wire length was less than 100 feet.

If it can afford it, I usually use the VFD cables/ reactors.
 
I'm no expert on this, but I would think the anticipated speed range might play into this, too. If you only run close to the motor's base speed, wouldn't standard cables be just fine, regardless of the distance?

Steve
 
Yea, it is somewhat depenant on Freq. and application But remember the VFD even running at 60hz is still producing harmonics that you would not have otherwise. So IMO unless it is cost preventive go with good VFD cables. It may prevent problems later and it's easiest to do on the front end rather than later.
 
PLC, after all that's been said on this subject lately, I'm a little surprised at your question.

But, to repeat, the answer is "it depends".

First, is there sensitive equipment close by that needs the protection of VFD cable?

Second, is the voltage 600, 480, 230, or 208? The higher voltages are more likely to need the suppression than the lower.

Third, is the motor an MG1P31 motor? Lower spec motors can sometimes be made to survive on VFD's with VFD cable and/or reactors/filters.

Fourth, are the motor leads in metal conduit, plastic conduit, or open trays?

See what I mean? Each of these has been discussed before, often with your participation in the thread. I don't mean to be a jerk here but consider this to be just a gentle nudge to do a little research before asking. OK?
 

Similar Topics

Hello, I've been trying to learn this a while now and still have not found out how this works. I have an Omron CJ2M PLC and an ABB ACS 355 VFD...
Replies
1
Views
228
I have a VFD rated for 125HP at 480V. After the VFD, there is a sine wave filter, then a 480/240 150KVA transformer, before the 100HP motor...
Replies
8
Views
3,127
We are looking into installing a well water pump (480vac, 25hp, 40FLA) with a PowerFlex 755 VFD. The challenge is that the well is located about...
Replies
13
Views
4,639
It sounds obvious, I know. The cost of good VFD cable for many motors over a modest distance is quite pricey. The manuals say to always use a...
Replies
16
Views
5,517
I am looking to use Lapp VFD cable and have configured it for the size I need in the attached file. But Which one of these 4 is the best choice...
Replies
5
Views
3,058
Back
Top Bottom