The small square connector you refer to is called a ferrule. They are available in insulated and non-insulated varieties. The one pictured is an insulated ferrule. A non insulated ferrule doesn't have the colored sleeve.
insulated-ferrule-but.jpg


I buy my ferrules from automationdirect.com. If you google wire ferrules you'll find tons of vendors however Automation Direct seems to have the best prices. You need a special crimper for ferrules, the crimpers you use for standard ring/spade conntectors won't work. I use crimpers from Wago - they have very nice self adjusting crimpers that aren't ridiculously expensive (they aren't cheap however) and give you a good tight square crimp. The automationdirect crimpers and the McMaster crimpers make a dimpled flat crimp. Both crimps are fine, its a matter of preference, but I think the wago crimpers are a little faster when doing lots of terminations.

260545032_tp.jpg


Ferrules add quite a bit of time to assembling a panel. Depending on where you are, they are not necessary, you can just insert stripped wires into the terminal blocks, however is some countries they are strongly recommended or required. They are not required in the US. That said, I prefer using them where-ever possible. They make the wiring much neater and if you plan on de-terminating and re-terminating the connection a ferrule will really help in preventing frayed wires.
 
Last edited:
Hi,

I'm new to automation and I'm using the Allen Bradley terminal blocks (IEC)-

http://www.ab.com/industrialcontrols/products/terminal_blocks_and_wiring/iec/iec_blocks_family.html

For now I'm inserting stripped wires but I'm pretty sure this is not the intended usage. I have seen wires used with these blocks terminated with a small, square connections but I don't see any mention of it on the AB site.

Who makes these?

Thanks

Your stripped wires should work fine in those terminals; ferrules are optional but usually recommended for very small wire sizes (example: 18awg or smaller). Some of my customers specify all sizes to be ferruled, some don't care.
 

Similar Topics

Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
Replies
9
Views
257
Hi everyone, I need some help I new with omron plc. I using plc CP1L. When I do the program it's good and the plc is function as program. But when...
Replies
1
Views
83
Hi there, Trying to get some ascii serial communications working via RS485 (COMMREQ functions). I have attached our wiring for the COM2...
Replies
1
Views
969
What's everyone use for I/O drawings on new installs. I am trying AutoCad Electrical, but can't download it due to a MS Office application running...
Replies
11
Views
1,307
I've been tasked with adding a 3-wire pressure differential transmitter to a system and drawing up the wiring to an existing PLC board. The...
Replies
7
Views
775
Back
Top Bottom