woodward egcp2 sync problem

robresti

Member
Join Date
Jan 2010
Location
Kecskemét
Posts
2
Hi Boys

[FONT=&quot]I may ask you to give me a support of EGCP 2.[/FONT]
I want to use it for stand-by (emergency-op) generators in order that it can syncronize two pieces of them.
[FONT=&quot]Speed control type is GAC 5120 and operated with normal opened (NO) actuator.[/FONT]

[FONT=&quot]The problem is that the synconization hasn’t been accomplished yet. [/FONT]

Further when I (short) close the pinout nr 55 and 65 the rpm is increased. While I close the pinout nr. 54 and 65 the rpm is decreased. So it happens reverse opposite the written instructions in manual.

The wiring is OK (double checked). What would be the problem? Where do I have to search the solution?

Thx for all the future help.

Regards
 
Swap the output cables over as you are driving in the wrong direction.
 
Thanks for your answer. The former problem was solved with a outer circuit.

The below new problem has been arised.

When the sign level was high at output 2 of EGCP2 to Gen. Breaker then it was closed.
But after that immedietly the sign level began to be low at output 2 of egcp2 so it was opened again.

The conclusion of 2 above written sentence the Gen breaker was switched into infinite loop.
I checked the type of contact was contactor.

The output sings are ejected In the next sequences
4 8 5 7 not5 1 2 not2 12 not7 not8 not12 8 7 2 not2 12 not7
The input sings are got In the next sequences
9 1 3 not 9 8 not8 8

You can see a presentation video (mp4) of I/O about the operation of it in order that you understand it well:
http://rapidshare.com/files/385576116/VIDEO_006.mp4.html

And further link you can see the I/O list:
http://rapidshare.com/files/385634924/EGCP2__I_O_list.pdf.html

In my opinion the mistake was in adjustment of data (given initial parameters in menu)
Thank you in advance you ideas.
 

Similar Topics

Hi Guys Does anyone know how to establish comms between RedLion DSPSX and Woodward 723 governar. The Aim is to Get all the Woodward status to...
Replies
2
Views
1,482
i have steam turbine control valve (moog) and woodward spc i want to caliberate spc according to my valve can anyone help me.
Replies
0
Views
1,879
Dear all, I have a generator / mains setup which is configured using the Woodward EasyGen3000-3500 and Woodward LS5 controllers. When running in...
Replies
3
Views
4,056
Hi All, I am working on a project using Woodward Easygen 3200 and a PLC for remote control. I have figured out how to run the generator remotely...
Replies
0
Views
2,485
i have a problem as there is "reverse KVAR" alarm apears at display what can i do and what the reason of this case?
Replies
4
Views
2,019
Back
Top Bottom