I was able to sucessfully convert a RIO panelview 1000E to a panelview plus using the panelview plus as a RIO panelview. It works fine.

Now my Boss wants me to create the same panelview application to Ethernet panelview and I cant figure out the addressing from the PLC to the panelview.

The block transfers are like this.

COP
Source N7:50
Dest #M0:7.200
Length 64


That M file has me lost and how it relates to the virtual block transfers in the 1000E panelview.

Thanks for any insight.

Bob
 
COP
Source N7:50
Dest #M0:7.200
Length 64

This one would be part of a "BTW", where the source data is N7:50 through N7:109 and the mapping inside the PanelView is probably "Block 1, 00 - 63".

You will also see some "BTR" type copies, where the Source is M1:7.x00 and the destination is an Integer file.

Find all the block transfer logic and make sure it matches up with the Block Transfer objects in the RSLinx Enterprise configuration, and you'll be able to substitute those N-registers when you create an EtherNet/IP application.
 

Similar Topics

Hello, I have a PID block in my program controlling pump speed in order to get a correct Differential pressure. The way I have it set up is the...
Replies
3
Views
1,254
I'd like to change the IP of a MSG instruction on the fly. I've identified the bits that change in the control block when I change the IP in the...
Replies
5
Views
4,712
I have found information on block transfers on the AB website, but no examples of the BTR instruction. I just found... copy, moves etc. does...
Replies
5
Views
6,618
With the data file of a BTW or BTR you can have a max of 64 words. Can anybody tell me why that is? With your logical rack and group set up your...
Replies
1
Views
3,771
Does any one know how to change the output of a PID block within RS logix to a time proportioned output for temperature control?
Replies
5
Views
7,676
Back
Top Bottom