Tom Hemeon
Member
I have a PV550 talking to a SLC 5/04 using DH+. The panel view has a numeric entry with a input and display tag which are the same. Both tag initial values in the panelview setup are .1. The tag address F8:24 is only used once in the PLC and nothing writes to it other than the Panelview. When I power down over night and start up the next day F8:24 goes back to .1 from 1.3. I replaced the battery in the PLC and then replced the PLC and Panelview with new ones which didn't help. The PLC and Panelview programs have been ok for 7 years. I reload the program in the PLC and everything is fine again until I power down.