Hi Guys,
Is there a way where you can wire two discrete output channels to a single solenoid?
I can think of several reasons to do this ranging from "I'm bored, let's do something" to "I have two PLC's and I need them to both turn on the same field device". The reasons you want to do this determine how.
Maybe someone who does safety circuit can enlighten me. Isn't a safety relay typically used in such situation?
OP said it's for a ESD (emergency shutdown valve), so the output from PLC is Normally energized and the ESD shuts when EITHER signal is lost. Correct?
I would not connect two outputs together, that is a good way to damage them if they are fighting each other. Your options depend on what you want to do. Is it an either or situation, or do both outputs need to be on to allow the Solenoid to engage? What if one PLC says solenoid off, and the other PLC says solenoid on? What needs to happen then?
It is certainly a solvable problem, but you have to set out your exact parameters first.
Stu.....