Hi all,
This may not be the right forum for this, but maybe someone can help me anyway.
What I have is a rack of MasterDrives and MM4's for various machine functions.
In the VISU application(WW InTouch 9.0 running on a PC627B)are keys set up as "drive download" buttons. When a drive is replaced in the machine, the technician addresses the new drive (P918=DP Address) and simply pushes the button on the VISU, which then accesses a DB in the S7 program with a sequential routine containing all the parameter changes and values needed for that particular drive slot.
This process works perfectly for the MM4's, but I have an issue when using the MasterDrives. Every time that I download parameters via the VISU to the MasterDrives, it appears that it has been successful. All parameter values are loaded, and written from RAM to EEPROM. As soon as I cycle power off/on to the drive units, all of the MasterDrives come up in status 21 (Download), preventing the drives from running.
Somehow parameter P60 has been written from a 7 back to a 6 (download).
It has been verified before power down that P60=7 in the RAM and the EEPROM. It was suspected at first that the PLC might be writing the new value in at power up, so the drives were downloaded, values verified, then drives were powered down, DP cable disconnected, and drives powered back up, it still changed this parameter value P60 to a 6, so I am relatively sure that it is something happening in the drive itself.
As soon as I enter the value P60=7 manually from the PMU, I never see this status 21 issue again (after repeated cycling of power) unless someone re-downloads the parameter set from the PLC via the VISU.
Thoughts please?
This may not be the right forum for this, but maybe someone can help me anyway.
What I have is a rack of MasterDrives and MM4's for various machine functions.
In the VISU application(WW InTouch 9.0 running on a PC627B)are keys set up as "drive download" buttons. When a drive is replaced in the machine, the technician addresses the new drive (P918=DP Address) and simply pushes the button on the VISU, which then accesses a DB in the S7 program with a sequential routine containing all the parameter changes and values needed for that particular drive slot.
This process works perfectly for the MM4's, but I have an issue when using the MasterDrives. Every time that I download parameters via the VISU to the MasterDrives, it appears that it has been successful. All parameter values are loaded, and written from RAM to EEPROM. As soon as I cycle power off/on to the drive units, all of the MasterDrives come up in status 21 (Download), preventing the drives from running.
Somehow parameter P60 has been written from a 7 back to a 6 (download).
It has been verified before power down that P60=7 in the RAM and the EEPROM. It was suspected at first that the PLC might be writing the new value in at power up, so the drives were downloaded, values verified, then drives were powered down, DP cable disconnected, and drives powered back up, it still changed this parameter value P60 to a 6, so I am relatively sure that it is something happening in the drive itself.
As soon as I enter the value P60=7 manually from the PMU, I never see this status 21 issue again (after repeated cycling of power) unless someone re-downloads the parameter set from the PLC via the VISU.
Thoughts please?