1794-fnd is use or not for this project

Join Date
Jan 2010
Location
hyderabad
Posts
21
Hi i am using plc of compactlogix 1769-L23E-QB1B and seven point i/o's are using(3 digital input(1734-IB8),2 digital outputs(1734-OB8),1 analog input(1734-IE8C),1 analog output(1734-OE4C))i am using 1734-AENT module using distrbute 24vdc to my point i/o's.my problem i want to take it 1794-FND or not.if didn't use 1794-FND this any problem appear please give a solution
 
As you have found, there is no such module as a 1794-FND. Even if there was, it is for the 1794 FLEX platform, not the 1734 POINT platform.

You may mean a 1734-FPD. This is a "Field Potential Distributor" and is meant to separate the power bus between DC and AC sections of the POINT assembly.

The best reference manual for selecting POINT I/O solutions is the POINT I/O Selection Guide, publication number 1734-SG001.

http://literature.rockwellautomation.com/idc/groups/literature/documents/sg/1734-sg001_-en-p.pdf
 

Similar Topics

Hey Everyone, After reading a lot on this forum and elsewhere I see not many are fond of the 1794-VHSC module. I can see to a degree as I was...
Replies
3
Views
145
I'm sure this question has been posted a thousand times on here but for me it was even funnier when I got to ask Rockwell / AB directly. My...
Replies
5
Views
160
Hello, a customer i support has DH+ RIO racks all over the plant. they use 1794-asb modules. today they had a rack fault out and go unresponsive...
Replies
0
Views
643
I have to configure new 1794-ADN Series C in my devicenet network. I have downloaded the EDS File and registered it. But while configuration in...
Replies
3
Views
1,034
Hi Newbie here :yeah: Can one of you experts help me with setting up a simple BTR and BTW to just test 4 analogue inputs 4-20ma (1974-if4i)...
Replies
11
Views
989
Back
Top Bottom