1756-ENBT and Logix5561 Controller

KyleKyz

Member
Join Date
Jun 2009
Location
Arkansas
Posts
8
Hi, I am trying to set up a 1756-ENBT so that I can communicate with the controller via ethernet. The F/W Rev. is 3.6 on the ENBT and I am running Ver. 2.42 of linx. I got an IP address loaded into the ENBT module using linx, but when I configured a driver, the device shows up as a yellow question mark with a red X on it. Can anyone tell me what the problem might be?
 
FYI....

As of today, version 4.8 is the most current ENBT version and version 2.56 is the current version of RSLinx. Might be worth the time to download the latest version of RSLinx too.

Then again, if you have it working......

OG
 
Because this kind of question comes up a lot I want to post a clarification:

In the RSWho browse in RSLinx Classic:

Device shows up as a yellow question mark: EDS absent from Registry.

Device shows up as a yellow question mark with a red X: No communication with device.

Don't chase around firmware or EDS files or anything else until you can get PING and HTTP to work, and until you get rid of the red X. The red X always means that the fundamental Ethernet or TCP connection is not being made to the device.
 
You are right. There was no connection, the link light was not lit up when a cable was in place, and I couldn't ping the module. But.....all those problems went away when I flashed the firmware. I don't understand why that fixed it though. Version 3.6 should have worked just as well as 3.9. Any insight on why that might have happened?
 

Similar Topics

please using the usb can i assign any ip address that i want ?
Replies
4
Views
150
Hi, I want to exchange data between two L55 PLCs using ENBT PLC1 is the main PLC and consist of 1756- CNB, L55 CPU and ENBT. Five remote I/O racks...
Replies
7
Views
1,028
Hey guys, I'm not super familiar with Cnet, so I'd like some insight from people with more ControlNet experience than I. We have a controllogix...
Replies
4
Views
892
I am looking into an ethernet drive network system using a Logix5000 system Version 20 and noticed that on the general tab of the properties of...
Replies
1
Views
1,133
I wanted to confirm with the Gurus that a 1756-ENBT can not create raw sockets. I'm using Rockwells Process Library's T_Sync to connect to an NTP...
Replies
3
Views
1,985
Back
Top Bottom