I need to find out the size (KW) of an AC motor so I can size up a VSD, the name plate is missing, was wondering could I measure the resistance of the windings and compare with other motors, my motor supplier says its not as simple as that.

Any help would be appreciated
 
Determine the frame size of the motor. Measure the shaft, base to center of shaft, spacing of holes on base, etc. Hook it up & determine the rpm. Frame size will be common for a range of hp sizes. Take it to a motor shop. If the label is gone it probably needs bearings anyway. Is it already connected to a piece of equipment? Measure the current of the motor while it is running and compare to FLA charts.
 
If the motor is connected to your machine and you can load the machine to the maximum it will ever see, measure the current under those load conditions and size the drive for those output amps. Or, to say it another way, size the drive by amps and ignore hp or kw.

Once you have those max load amps, you will need to estimate how much short-term overload torque will be needed. If the operation is smooth with no sudden load upsets and no sudden speed changes, buy a drive with only 10% short-term overload capacity. These are usually called "variable torque" or "normal duty" drives.

If, on the other hand, your operation involves a lot of sudden speed changes or heavy shock loading, buy a drive with 50% short-term overload capacity. These are usually called "constant torque" or "heavy duty" drives.

Actually, sizing a drive by current rather than power is generally the better way to do it anyway so don't struggle too much to find the motor's power rating.
 
If you may run your motor and measure its current you may determined FLA from following rule - FLA = 1/3 idle current. Ofcourse the relation is approximate.
 
...and if you happen to have individual motor PFC capacitors make sure you check the current before them, motor side. Especially important on a motor with little load. VFDs & PFC caps don't mix so make sure you do not have them on the load side of a drive.
 

Similar Topics

I have been wanting for along time to experiment and get more involved with some servo / motion control to learn and expand my control knowledge...
Replies
10
Views
2,005
Hi everyone ! A multiconductor wire 4x2,5mm2 would be ok ? Normally a 10hp - 400V motor would pull 16-17A A 4x2,5mm2 wire could carry around...
Replies
2
Views
1,850
Because of 3 or 4 posts with errors on this subject, this US National Electrical Code admonition needs repeating: NEC Handbook Article 430.22...
Replies
10
Views
5,806
Can anybody lead me to a table or calculator for DC Motor Cable size?
Replies
2
Views
2,356
I was wondering if anyone knows the wire size for a 3 phase 200hp motor for an air comp the uglys book only goes to 150hp motors also where...
Replies
6
Views
3,328
Back
Top Bottom